trying to install the CT30..Heat pump with Aux heat and A/C. right now the current lennox thermostat 51M32 has the following wires installed and
Contact/ Color
R- Red Wire
G- Green Wire
Y1- Yellow
W1- White
C- Black
now with CT30 installed the system does not switch to heat mode, just stays in a/c..its not switching over and as i understand i needs a Orange wire to do so but no orange wire on the old thermostat, wire is there but not hooked.
Went upstairs and checked out the zone control. EWC NCM-300
Zone 1 TStat
C-black
w- white
y-yellow
r-red
g-green
Zone 2 TStsat
C-Black
W-White
Y-Yellow
R- Red
G-Green
on the System side of zone control
there is an Orange wire coming from outside unit but no orange wire from zone control to Thermostats..so how can the system change with out the O wire..Looks like to me i have been running Aux heat to heat the house as primary heat and the heat pump never worked...
This is a 6 yr old house and this is original wires and wired that way.
Can i just run a jumper wire from the TStats to the system side O wire?