OK, it turns out I had a power problem and didn't realize it.
My old Aprilaire unit didn't need batteries and had an existing c-wire connection, so I though the standard "5-wire Heat/Cool" setup would be all I needed.
After I wired the 3m-50 everything seemed to be working except communicating with the radio from my network.
I could take out the batteries and appear to still have power, but it turns out I wasn't taking out the batteries for long enough - it took a full 30 secs or so for the 3M-50 to fully discharge and power off.
So I actually did NOT have power to the thermostat.
With a meter I could see that I had a solid 24VAC across C-RC, but only ~1V across C-RH, so the old Aprilaire seemed to be drawing it's power from the A/C air handler in the attic and not from the furnace in the basement.
The 3M-50 seems to want power only from C-RH - is that correct?
To solve my problem I jumpered RC and RH. Now heat and cool still work and after reprovisioning the radio the Thermostat for Windows program can see the thermostat.
I'm not sure what are the implications of jumpering RH-RC, but I was getting no power from the furnace, only from the A/C air handler.
Can anyone give any guidance?