HVAC has no C output

This section will help you power your thermostat during the install process

HVAC has no C output

Postby EnoughWithTheCWire » Sun Jun 10, 2012 9:22 am

I am one of the lucky ones that has his HVAC in the craw space above his house (please note scarcasm). It is a b%#*% to get up there and after finally finding where the wires from my 3M-50 goes to, it saddnes me to see there no C output. Now, I know that if my HVAC has power it has Common Power, but I don't know where to get it from. I have an extra blue wire that is unplugged at both sides, but I am out of ideas of where to connect it to.

There are no capped wires and there is no output for "C". I have dedicated outputs for "G", "Y" ,I think the next one is "W", another random green wire, and "R".

Any ideas?
Attachments
Zoom Out.jpg
Zoom Out
Zoom Out.jpg (187.61 KiB) Viewed 611 times
2.jpg
Close Up 2
2.jpg (255.9 KiB) Viewed 611 times
1.jpg
Close up
1.jpg (233.75 KiB) Viewed 611 times
EnoughWithTheCWire
 
Posts: 1
Joined: Sun Jun 10, 2012 9:07 am

Re: HVAC has no C output

Postby blaine » Sun Jun 10, 2012 9:44 am

1. See if you can find the 2 wires going out to the compressor; one of those 2 wires goes to Y at the thermostat and the other one is the C wire that you could tap and use that spare wire to get it to the thermostat.

2. Or, you could use a 16VAC, or 18VAC, or 24VAC adapter (100ma or more). Connect one of the wires to the R at the HVAC (the wire that goes to RH at the thermostat) and the other adapter wire via a spare wire to the C at the thermostat. (16 or 18 preferred).

3. You could also use the 17VAC doorbell transformer if available; connect directly to the transformer.

R to RH and RC connected for 24VAC power
G to G for fan
W to W for heat
Y to Y for cool compressor
C to C for 24VAC common